Pass through
I have a 5kw quattro 24v, 800amp battery bank is smart lithium. Generator is running and charging the battery bank at around 52%
The charging is in bulk, then the charging has stopped and the quattro is in pass through mode after around 30 minutes.
This is a random thing that doesn't happen often, I have to manually turn off the quattro and restart it. Restart the genset and it will go back to bulk charging.
I am looking to find out why, what settings are required to stop this issue.
Thanks Michael winand, yacht NEBO
JohnC avatar image
JohnC answered ·
Hi @Mfw
Gensets can often be troublesome if not set up correctly. And I find at high charge rates can get rejected by the Quattro/Multiplus, but might be fine just passing through loads. Take a look through this.. https://www.victronenergy.com/live/multiplus_faq
You mention 'passthrough'. Do you see this indicated somewhere, and are loads actually being served by the genset, not the inverter?
A little more info on your system components might help with diagnosis too.
mfw avatar image mfw commented ·
On pass through the load is on the genset, no charging while in pass through mode.
JohnC avatar image JohnC ♦ mfw commented ·
@Mfw
Where do you see this "pass through mode" indicated? You running ESS? If so, that's your problem. We can't see from here..
mfw avatar image
mfw answered ·
System has a CCGX. This is showing the charge current. Batteries are 4 of 200Ah 24v smart lithium generator is a 8kva, the quattro is changing at 120amp.
Thanks for your help Michael