clay avatar image
clay asked
MPPT 100/30 voltage compensation
What is the maximum increase in voltage that a MPPT 100/30 can put out to compensate for the voltage drop between the charge controller and batteries? The charge controller receives battery voltage information via a BMV-712. I measure a voltage increase at the controller of 0.5 to 0.6 volts above the programmed voltage at a charging current of 15 to 20A but this is not adequate to achieve the target voltage at the batteries. Is this the maximum increase possible?
MPPT Controllers
Michelle Konzack avatar image Michelle Konzack commented ·
I suggest you to install the maximum size of wire you get into the Co acts at the SmartSolar. AFAIK it is 25mm² which I will do to, because even 16mm² become warm (you can realy feel it it you take the wires in the hand)
Michelle Konzack answered ·
I have the same problem.
My 4 battery sets have seperate BMV702 and are connected via 70mm² of 2,5m lenght to a (huge) power rail wich support 2200A where also my three SmartSolar (70A + 100A + 100A) are connected using 16mm² wires of around 1,5m lenght.
Under full charging load I get a voltage drop between the SmartSolar and the Batteries of around 0,5-1,8V especially if I get in the same time also windenergy (3x 2000W + 2x 700W).
This give a charging current of around 500A @28V.
I have compensated this by increasing the Absorbtion Voltage from 28,8V to 29,6V and the Equalising Voltage is still unchanged on 30,6V.
P.S.: I use SOPzS cells and have 2940Ah @24V currently, but this will increase to 7320Ah @24V with in total 8 sets.