I know each 3kva MPII (48v) needs a 50a breaker for grid input and load out (double poles for split phase). Can a MPII setup in split phase actually pass through 45-50a (11kw) when just using grid power, no assisting or charging?
I know each 3kva MPII (48v) needs a 50a breaker for grid input and load out (double poles for split phase). Can a MPII setup in split phase actually pass through 45-50a (11kw) when just using grid power, no assisting or charging?
@Paul B thanks for the response. It’s incredible that small 3ka inverters like than can pass the full 50a through. Amazing, glad I’m looking at this for my home backup for split-phase. Obviously manually use less power when grid is down but awesome power passing through when grid is up.
77 People are following this question.