trinle avatar image
trinle asked
Victron BMS-712 Shunt Shut-off
We have a BMS-712 with 2x100 Ah Relion Lithium batteries and a Renogy solar setup (3x160w panels and a 40amp Renogy Rover Charger Controller.
Also have a 3000w Power TechOn PS1006 installed.
The issue us when I put a load on the system using the Inverter; say a 1300w toaster oven, the whole system will shut down and kill the Inverter within 15 seconds?
The reason for posting on this forum is that when that happens, I hear a click sound coming from the box where I installed the Victron Shunt?
Seems the shunt is shutting off the current under heavy loads. Is that even possible?
The whole system works fine under light or medium loads.
I measured the voltage of each 12v battery under this condition and the voltage is rock solid. At first I thought there was an over voltage on the batteries causing them to shut down for a few moments but this was debunked.
Victron settings for Li Relion batteries.
Battery Capacity 200Ah
Charged voltage 14.0v
Tail Current 2.00%
Peukert Exp: 1.10
Charge Efficiency Factor 99%
Current Threshold: 0.10A
Everything else is Defaults....
Any suggestions????
Also is there a tech support number in the USA to call for Victron Engery?
Thank You for your input.
BMV Battery MonitorLithium Battery
cardreader avatar image cardreader commented ยท
I had a very similar if not the same problem . Solved by upgrading inverter leads to 50mm cubed (?thick as little finger) cable and had no problem since .Worth a try.
0 Likes 0 ยท
Paul B avatar image
Paul B answered ยท
The Victron shunt has NO switch of any kind in it, so it cant be the shunt
The only way it could be would be the shunt joins have a faulty weld but I have never seen that
If I were you I would do some more testing
ie
ByPass the shunt and see in you get the same issue under the same load. The shut down issue will be something else.
so Remove the shunt Join the two big wires and test some more.
I.e. Try measuring battery voltage at the connection to the inverter under load.
chrisryan43 avatar image
chrisryan43 answered ยท
I have just started having a very similar issue. Every so often i will lose all power from my LiFePO4 battery. It tends to be when a new load is added but it is very intermittent and not always a large load. I knew the problem was something close to the battery because the BMV-712 would lose it's SOC meaning it must have lost power. So either it was the battery shutting itself down or the BMV-712. The BMV-712 has been over reporting voltage recently (around 500mV - even though a multimeter at the shunt proved the correct voltage) and i thought it seemed a bit warm the other day so i was starting to suspect the shunt.
The next step is to bypass the shunt to be 100% sure. What was the outcome with your issue?
kai avatar image kai โ™ฆ commented ยท
Can you confirm that the shunt connection is all good? e.g. no issues with crimping from cables to lugs, lug contact area clean (no oxidation), lug is adequately torqued down.
0 Likes 0 ยท
Stephen Otto avatar image
Stephen Otto answered ยท
Iโ€™m guessing that the sudden load causes the voltage to dip low enough that the inverter is triggered to shut down to prevent over-discharge. Pretty common issue. Check your inverter settings.
ianddindustries avatar image
ianddindustries answered ยท
Hi
I had an issue very similar to this and it turned out to be a loose terminal inside the battery between the cells. The problem was intermittent and only discovered by watching each cell voltage when it was faulting. As soon as the terminal was tightened it solved the issue
wobby avatar image wobby commented ยท
Iโ€™m having a similar problem with my lithium battery. How were you able to check the connections inside the battery. Mine has built in management for over, under and low temp.
0 Likes 0 ยท