Can MultiPlus 12/1600/70 work below 180V? to 150V ?

Due to electricity shortage in Ukraine, we have a lot of sites where mains voltage is 160-170V.
VE Configurator allows minimum 180V.
We need as air to low it to 160V.
Minimum voltage when charge are working also from 187V to 165V.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

Unfortunately you can not configure the multiplus to operate at such low input voltages.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

oles avatar image
oles answered ·

Yes, we realize that with a low input voltage, we will not be able to use the maximum charging current. This charging current limitation can be embedded in the MultiPlus firmware - when low input (below 180V) is choosed then charging current limitation will be applied. For example:
170V - 70%
160V - 65%
150V - only 50%

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Yes, we realize that with a low input voltage, we will not be able to use the maximum charging current

It is also about the voltage produced at the output (LV side) of the transformer not being high enough to charge the battery.

The only charger that will work on such low ac voltages, is the Centaur charger.