Connecting to the grid, home system with 48v PylonTech batteries, multiplus2 and off peak charging.

I have my home batteries set up to provide off peak power to my heat pump but I really want it to feed into the house, could someone direct me to the instructions to set this up. I understand I need a current sensor but I’m not sure how and where to configure it, many thanks.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
mazzen avatar image
mazzen answered ·

Sounds like you want to setup an ESS? A good starting point would be this:

https://www.victronenergy.com/live/ess:quick-installation-guide

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Richard Weir avatar image Richard Weir commented ·
I have watched that and, unfortunately don’t see how to get the batteries feeding into my home circuits with out connecting them directly to ac out1 or 2. I have altered the Power Assist flag to ON but need some assistance from there. Thanks.
0 Likes 0 ·
dj-dulux avatar image dj-dulux Richard Weir commented ·
Takes a bit to get your head around this so ask away as needed, the AC Outs are optional if you want circuits that are battery backed up (essential loads), you only need the AC In connected for ESS, its 2 way, will charge and discharge back into your consumer unit to run the house on off peak electric. You will need an energy meter on the tails too.


Dupe...


0 Likes 0 ·
Jason - UK avatar image
Jason - UK answered ·

@Richard Weir I do currently have my current sensor on my mains tail between the meter and the main distribution board as shown on my below schematic. My whole house runs though my Multiplus therefore really I do not need a CT sensor as the sensor on the AC-in will do the job but as I have the system set up for power assist for the EV charger, I kept the CT sensor on the incoming mains tails between the meter and the main distribution board to allow power assist.

If you have loads on the AC-In side of the Multiplus, then put the CT sensor on the incoming mains tails to provide power assist to the loads you have on the AC-in side of the inverter and set the powrr assist to 1.0 in VE config.

4329-bhv-zz-xx-sc-e-6000-xref-a1.jpg

1669719535221.png



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Richard Weir avatar image
Richard Weir answered ·

001f1962-2995-4087-b47f-75e93a4ba458.jpegHi @Jason - UK thanks once again for your help.

I have adjusted the inverter settings as per your, but kept my voltages slightly different. I see that you have all of your home circuits connected in a straight through design but I wanted to set up a parallel design where the batteries feed back to the circuits via the AC IN 1. Can you help with that? Thanks



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image Jason - UK commented ·

@Richard Weir do you have a schematic of your system? I'm assuming you have set up the ESS assistant, if so, then with the CT sensor on your incoming mains cables, you should nearly be there if not working already.

1669725817733.png

0 Likes 0 ·
1669725817733.png (139.1 KiB)
Richard Weir avatar image
Richard Weir answered ·

Hi @Jason - UK I have the CT installed now and wired to Aux1 but don’t seem to have any further info on the screen about its connectivity or use. I’ve ticked the box in the config and uploaded the new file but again no change in how it’s working. I’m getting about 2vdc from the ct itself, just wondered if it’s got a specific polarity? Thanks richard.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image sharpener commented ·
PMFJI but yes, so try turning the CT round on the tails or swap the connections at the inverter.
0 Likes 0 ·
Jason - UK avatar image Jason - UK commented ·

@Richard Weir What CT sensor do you have? Is it the 100a Victron CT sensor with the 3.5mm jack on the end? Odd you have it connected to AUX1.

Under grid code settinfs in VE config on the 2nd tab, do you have the ‘Use AUX1 for grid control’ (or words to that affect) selected?


0 Likes 0 ·
Richard Weir avatar image Richard Weir Jason - UK commented ·

this is the CT Ive fitted




224bc11f-10ab-4dfa-a813-82f47d92c6f3.jpeg

0 Likes 0 ·
Richard Weir avatar image
Richard Weir answered ·

1670492307225.png


Here is the grid set up




1670492307225.png (643.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Richard Weir avatar image
Richard Weir answered ·

1670492427444.png


Here are the other parameters


1670492427444.png (629.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image
Jason - UK answered ·

@Richard Weir send me a email at ________ and ill send you my mobile number.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.