System description:
  • 2 paralleled MP II 48/5000s
  • Single phase
  • ET112 energy meter
  • All loads on ACout1
The current reading of the ET112 is quite different to that of the MP II current sensor. The differences point to possibly a calibration and a scaling issue. It appears that ET112 is correct when compared to a clamp meter, which means that the MP II is most likely incorrect.
  • Blue circles are when the grid fails, and both read Zero
  • Magenta circles highlight examples of variances
The same phenomena are being seen on other systems as well, with various versions of inverter firmware. Single and 3 Phase systems, all with the MP II 48/5000
How can this be fixed?
Multiplus-IIinput current
Rob Duthie avatar image
Rob Duthie answered ·
Hi
This is expected and known, the current coils in the victron are not that accurate, as they are not a metering device were as the ET112 is a proper metering device with a high class accurate rate.
Also the clamp meter is worse, so dont expect much as per Victron documents its only a rough estimate its not a measuring METER!!! as such
Regards
Rob D
NZ
gnagflow avatar image gnagflow commented ·
Can’t believe that the Multiplus has a 2 Amps inaccuracy,
i compare the Victron current values regularly with bms values, and most of the time they are very similar.
who cares: everyone who want to know if the data shown could be real. I am very interested in those differences.
anieuwstadt avatar image anieuwstadt commented ·
Hi Rob,
I have not had issues with the clamp meters that you have spoken of. In this case, the ET112 and the clamp meter are very similar.
Inaccurate measurements will have a negative bearing on the correct operation of the proportional–integral–derivative control loops inside the inverters and the Cerbo GX.