As others have noted, meeting new LFSM-O standards is currently a sticking point for Multiplus G99 compliance. For me (and anyone with kit on order) the crux issue is whether or not a firmware update is likely to provide a fix. On this thread, @Rob Duthie says it's a hardware problem, @ejrossouw says firmware will solve it:
https://community.victronenergy.com/questions/160177/victron-inverters-no-longer-approved-for-uk-dno-gr.html
Below is a the relevant part of a report from an NG engineer - can anyone make sense of this and does it help indicate whether its likely to be a firmware or hardware issue?
Thanks
· Limited Frequency Sensitive Mode – Overfrequency test:
Failure (based upon requirements of ENA EREC G99/1-9)
LFSM-O is one of the technical requirements that ESS were previously exempt from. From September 2022, this is no longer the case.
Notwithstanding what is written in BS EN 50549-1, ENA EREC G99/1-9 makes it clear [in Section 11 (Type A Power Generating Module Technical Requirements), Figure 11.3 (Active Power Frequency Response capability when operating in LFSM-O)] that the Registered Capacity (Pmax) should be taken as the reference power (Pref), and not the actual AC output power at the instant when the frequency reaches the threshold (PM). Victron have seemingly used the latter.
The results for the ‘Test sequence at Registered Capacity >80%’ seem to meet the requirements of the EREC (calculated droop is 9.88%), but those for the ‘Test sequence at Registered Capacity 40% - 60%’, unfortunately, do not (calculated droop is 19.76%).