6 or 2 mppt contollers
Hi all
just getting started on my full time off grid setup
i have 6x qcell 480w panels and will be getting 2 x 5kw 48v lifepo4 battery packs
I will be living and working from my rig, so redundancy is important
trying to decide on mppt contollers, I have a 40 foot school bus that I’m converting so space is not a big issue
the pales have 11.2a short circuit current and 54v open circuit voltage
i think I could go wit 6x 100/20 or 2x 1 x 150/70
the former is cheaper, so other than having it run more cables through the roof and more ve.can cables, is there a downside to using 6 MPPT contollers?
thanks
mark
MPPT Controllers
klim8skeptic avatar image
klim8skeptic answered ·
What is the Voc / Vmp of the panel?
I imagine that 1 panel would not have a high enough Vmp to charge a 48v battery.
Likewise 3 panels in series would be over the mppts 150v pv input voltage limit.
Please use the Victron online MPPT calculator..
@Mark Anderson
To add, MPPTs require panel input to be higher than actual battery voltage +5V to start charging.
Try 3 parallel strings of two panels into a single 150/70 in the calculator.
Mark Anderson answered ·
Thanks for responses. Here’s link to panels https://www.q-cells.us/dam/jcr:261eb7ed-4eb2-4049-a64e-44da63fdf056/Q_CELLS_Data_sheet_Q.PEAK_DUO_XL-G10.3-BFG_475-490_2021-08_Rev01_NA%20(1).pdf
Vmpp is only 45v, so I’m figuring 3 strings if 2 and 3 mppts would be best for max flexibility.