andrii avatar image
andrii asked
Not mixed solar
Hello guys! I have several systems for multiplus and quattro with pylontech batteries (us2000c). I have the following problem: when setting the keep batteries charged (when the batteries are 100% charged), solar energy is not mixed into the load. I use MPPT Smart Solar controllers. Please help me solve the problem. In other modes it's correct. Thanks.
MPPT ControllersMultiPlus Quattro Inverter Charger
marekp avatar image
marekp answered ·
@Andrii
If you have ESS assistant loaded select "DC-coupled PV -feed in excess" to ON.
andrii avatar image
andrii answered ·
But with this setting, excess solar energy will be fed into the grid, which I do not need.
6 comments
marekp avatar image marekp commented ·
@Andrii
If you set the "Maximum feed-in" to 0W or even negative number it will not feed the grid.
Just try it as a test briefly. Don't leave it on, it helps narrow down the cause.
Usually with keep batteries charged, only when the batteries are full-ish, solar would power some or all of the load, the delta coming from grid.
In your case is it all coming from grid?
andrii avatar image andrii nickdb ♦♦ commented ·
Yes, in my case is it all coming from grid. When DC- coupled PV is ON, solar energy mixed, but it's OFF, solar is 0 or 5W. When I do this several times, the system will start working correctly, but after a while it may repeat and the solar energy is again 0W
nickdb avatar image nickdb ♦♦ andrii commented ·
It may be worth taking a meter and when it is happening, measure the voltages at the mppt, battery and multi terminals and see if they agree and how they compare to the CVL the BMS is sending.
Alexandra avatar image Alexandra ♦ nickdb ♦♦ commented ·
@Andrii
You can also set the feed in on and set to 0w.
andrii avatar image andrii Alexandra ♦ commented ·