question

mlawranceowen avatar image
mlawranceowen asked

Damage to Multiplus due to reverse polarity input

Hi,

I noticed in the manual for the Multiplus that it states reverse polarity would be damaging to the unit ("Reverse polarity on these is a fatal error that will destroy the unit"). Generally people seem to use a mains plug tested to check for reverse polarity and then use an adapter hookup wire to reverse it back if if needed. However, to do that would mean the reverse polarity input has already gone through the Multiplus....is this an issue and if so, whats the best way around it?


Cheers, Mike

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

Hi Mike,

Don't worry, the reverse polarity is for the DC side (batteries connection) on the AC side the inverter won't even complain if it is a single phase installation.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mlawranceowen avatar image mlawranceowen commented ·

Fantastic, Cheers

0 Likes 0 ·
rolandka avatar image rolandka commented ·

Does the Multi pass it through? I mean if we have reverse polarity on the input side, is the output side on the Multi effected? Does it "correct" or swap the N and L?

0 Likes 0 ·
mihair avatar image mihair rolandka commented ·

The output will be reversed too

1 Like 1 ·
rolandka avatar image rolandka mihair commented ·

Thank you!

0 Likes 0 ·
Cansin Sari avatar image Cansin Sari commented ·

Hello there,

if you want to use the Inverter in a power mode, so when half of the Energy comes from the grid and the other half from the batteries, is the battery also effected? So is the battery limiting the AC Out?