I have a Multiplus II 5KVA and 3 x 3Kw 48V Pylontech Lithoum batteries.
Multiplus II 5KVA with 48V battery has a maximum power peak of 9Kw.
Does the fuse between the battery bank and the invertes have to be size for the nominal current (104A) plus a 25% security factor or for the maximum peak current (188A) ?
Thanks
Multiplus-II
kevgermany avatar image
kevgermany answered ·
There should be a fuse size in the manual. But it needs to be sized above peak. Same goes for cabling.
The startup current with the big capacitors inside is very high.
I just checked the manual. Section 4.2 says 200A fuse, 70mm square cables up to 5M, 2*70mm over that.