dgmar-ni avatar image
dgmar-ni asked
Solar chargers don't work under ESS
Good day,
Two solar chargers Smart MPPT 150/70-Tr and Smart MPPT 250/70-Tr don't charge the batteries under ESS mode. On VRM the system shows this:
I have set the system to not sell any PV excess to grid. However if I set the system to sell the excess, controllers do start to charge and export PV excess to grid:
Moreover, if we disconnect the VE.Direct cable from both controllers to Venus GX, they do charge battery bank but system doesn't run under ESS:
Any clue of what could be wrong on configuration? I need to set the system up properly for ESS and I have compared all parameters with other systems I have installed that seems to run properly on ESS.
Thank you in advance for your help.
MPPT ControllersESS
7 comments
In situation from the first image, if you disconnect AC In, does the MPPTs start to provide power?
What else you have in that system?
Maybe put some screenshots with some of the settings.
dgmar-ni avatar image dgmar-ni seb71 commented ·
Here are some screen shots for the system's configuration...
seb71 avatar image seb71 dgmar-ni commented ·
Can you try this:
With the VE.Direct cables connected between the MPPTs and Venus GX.
It does not:
AC In disconnected but charge controllers don't work.
I just changed the firmware version for the Quattros and now is working running on solar:
The firmware version is 433:
The ESS doesn't work with the latest version of the Quattros.
duto69 avatar image duto69 seb71 commented ·
in my case, if I disconect AC MPPT start charge. Do you know, where is problem?
dgmar-ni avatar image dgmar-ni commented ·
Device list:
Both charge controllers have been disconnected as you can see they have more than one day since last connection.
dgmar-ni answered ·
It turns out that I didn't realize when I changed the firmware version the ESS assistant was removed. But once I installed it It didn't work. So again this is the behavior now without rhe ESS assistant:
But no ESS assistant installed:
I have updated everything all devices to latest firmware. What is the proper assistant to use?
ESS (Energy Storage System)(017E) didn't work for this firmware version:
dgmar-ni answered ·
I have reinstalled the ESS assistant and seems to be working now:
dgmar-ni answered ·
Settings on remote console:
What batteries do you have? What are the charge settings of the MPPTs(VictronConnect)?
seb71 avatar image
seb71 answered ·
The charging settings in the MPPTs must be fine since they are charging when the VE.Direct cables are disconnected from Venus GX.
Can you post screenshots with the charger settings and ESS settings from Quattros?
Also, disable "Has DC system" from Venus GX settings.
seb71 avatar image
seb71 answered ·
DVCC is enabled?
What is the charging current set there (if enabled)?