sasunnu avatar image
sasunnu asked
Multiplus-II Wire Size Smaller Than Fuse?
I've purchased a Multiplus-II 24/3000/70, and the manual recommends a 300A fuse, but then only 50mm2 wire size - am I correct in thinking this would be undersized for a fuse of this size?
I'm also wondering if anyone has used a smaller fuse of say 175-200A?
Multiplus-IIfuses
kevgermany avatar image
kevgermany answered ·
I'd stick with the recommended size. The start current on the multiplus can be very high as its capacitors charge. If you do get a short, a 300A fuse will blow quickly.
5 comments
sasunnu avatar image sasunnu commented ·
Thanks. The 50mm 2 wire would be undersized for a 300A fuse though, wouldn't it?
kevgermany avatar image kevgermany ♦♦ sasunnu commented ·
Guess it depends how you're using things. Here not.
sasunnu avatar image sasunnu kevgermany ♦♦ commented ·
Sorry if my questions are dumb, I'm quite new to this. Do you mean if I am not running the multi to full capacity then 50mm2 would be sufficient? The 50mm2 cables I am looking at have an amp rating of 246 at 30oC, and in all the wire size/maximum amperage charts I have seen 50mm2 is always under 300A.
munga avatar image munga sasunnu commented ·
On a good day the MP2 will only draw ~150A (continuous) to make its 3000W so your 50mm2 cable is safe. The fuse rating is, as @kevgermany points out, to deal with high start up currents of the MP2 etc. If you have a short circuit, this will exceed 300A very quickly and the fuse will blow (very quickly) and your cables will also be safe.
@munga said it for me, thanks.