wolle4000 avatar image
wolle4000 asked
AUX1 at Victron Quattro
I want to use my AUX1 from my Victron Quattro to disable charging with an assistent( charge current control assistant ).
Do I have to connect the two wires of the AUX1 to switch it on or off.
or can I give also 12V to the AUX1 to switch it on or off ?
wkirby avatar image
wkirby answered ·
Connect the wires to turn it on or off.
Please do not put 12V up it.
4 comments
wolle4000 avatar image wolle4000 commented ·
then I will need a 12V relay ?
wkirby avatar image wkirby ♦♦ wolle4000 commented ·
If your source signal is 12V then yes, a relay would work.
Alternatively, you could use an optocoupler, solid state and perhaps more elegant.
wolle4000 avatar image wolle4000 wkirby ♦♦ commented ·
This is a screenshot of the charge current control assistant .
But here I have to insert a voltage on the AUX-1 ?
If I have a relay (Potentialfree) on the AUX-1 there is no voltage ?
Or do I see the things wrong?
Thanks you your help.
Your signal is 12V which is too high, so the need for a relay or opto coupler.
You can see on that page that there is mention of an internal pull-up, so you can have the 5V from the internal pull-up and the 0V when your relay contact closes.
Then set your DC charge current values for each state.