HI All,
I was charging my batteries on my boat today, as usual. Noticed a burning smell, and traced to the inverter area. I turned off the generator input, and all conntinued fine, the smell went away.
I tried re applying the genset input, and the unit tried to switch from Inverting to Bulk, and seemed to fail. The was a fairly loud switching noise (may be normal) and the unit turned off. It seemed to restart, and the Float and Temp led's flashed for a second, and the attempt to change to Bulk restarted, and failed again in this loop. I turned off the genset input again, and now the unit is dead, it wont turn on at all.
Can anyone please help with any basic troubleshooting, or is this likely a pro service job?
editwiz avatar image editwiz commented ·
Product:
Quattro 12/5000/220-100/100 120V VE.Bus
SKU:
QUA125021100
Serial number:
HQ2105MBVP2
Complaint:
Reason for return:
Report from client:
While our Trawler was underway. I had the Generator running while Master-Slave Quattro’s were charging Lithionics ESS system. The alternator was derated for 50% output contributing 180 DC Amps to the charging as well when the Master Quattro failed. Burning smell detected by my wife while handling lines outside. I mediately isolated the DC input to the Master Inverter. I have configured the Slave as a stand-alone to charge the Lithium however I had to send the Master Quattro in for repair. I see that I'm not the only one struggling with this issue.
I was running current firmware
Installation date: 2021-06-25
Failure date: 2022-08-23
Firmware update: Current
Installed firmware version: V497
Warranty claim: yes
Is there a follow-up by Victron on this issue. I have concerns that my Slave may fail as well.
Zombonz,
How did you resolve your Quattro catastrophic/burn failure?
Paul B avatar image
Paul B answered ·
you will need to return it to the dealer you purchased it off as by the sound of your issue it will need repairing
zimbonz answered ·
Thanks. I realise that is likely the obvious answer, but that is not possible for me, as I am half way around the world from the original dealer. But yes I suppose it does need to be looked at by Victron. I am detecting 13v input from battery but unit is not powering on. I had hoped there was a fuse somewhere that might be a culprit to start with, but it appears not. Thanks for taking the time. Cheers
mike-a avatar image mike-a commented ·
Did you ever find the source of a problem or solution? We seem to be having a similar issue.
editwiz answered ·