would like to ask if victron multiplus 12/800/35 is good for charging lifepo4 batteries? Till now I had agm batteries but i would like to change. 95% of the time I charge batteries from solar and an alternator (dc-dc charger from victron). But from time to time I plug in.
Many thanks!
Multiplus-II
Paul B avatar image
Paul B answered ·
as long as the setting are set to lithium it will work fine with lifepo4 batteries
123fish answered ·
But how do I set to lifepo4 on a victron multiplus 12/800/35? I know that i can set it on solar charge controller and on dc-dc charger, but i dont know how to do it on multiplus.
Thank you.
You have used Victron Connect before?
Open it up, click on the 3 bars at top left, choose demo library, pick your inverter charger.
Test drive the settings.
123fish avatar image 123fish klim8skeptic ♦ commented ·
i am using it all the time, but you can't connect multiplus to it.
https://www.victronenergy.com/inverters-chargers/multi-500-va
we are talking about this one, 800w.
123fish answered ·
https://www.victronenergy.com/accessories/interface-mk3-usb
is this what I would need to set settings to lifepo4?
4 comments
A Mk3 is probably the easiest option.
Further reading.
are there any other options? Because i dont find mk3 to be in stock nearby.
klim8skeptic avatar image klim8skeptic ♦ 123fish commented ·
You could perhaps use a GX device (or a Raspi) to control stuff.
In all reality, you will initially need a Mk3 to update your multi, to a firmware version that a GX device can configure / control.