On-grid (50 Hz, 230V single phase) ESS System MPPT and batteries on DC, with CCGX and Quattro 8k feeding load, with mains/utility power on AC-IN1 and generator (49-52 Hz controlled) on AC-IN2.
I have been previously advised to put gen on AC-IN1, but as mentioned by other posts, I need the mains input to always have priority. I have LOM to B on mains and no LOM on gen, and enabled wide voltage and frequency and UPS function in the ESS assistant.
The power would go off, and the gen starts by independant control. The ESS system does not use the gen power right away but first inverts power from batteries and MPPT until batteries reach 96%, at which time the AC-IN2 (which have already had Gen power for a while) is engaged. The system drops the load for about 30 seconds when engaging gen power, despite no wide frequency or voltage swings taking place. Very irritatiing, but not the worst, as this usually happens not too often. Current limiting keeps the system from using too much gen amps, so the load is fully carried, and a few spare amps is used to charge batteries together with MPPT power.
But then, at random intervals, it seems the amps, (but not V, like in a disconnect) are dropped from the Quattro input AC2 through to the output. The input voltage stays normal or go up a few Volts as a 4kW load is dropped for a few seconds. No warnings or any frequency or load changes are evident. It might be a 30 second problem that does not show up at 1 minute recording intervals in detail.
See below zoomed images of the recorded parameters at the time of one of the drops. It happens every 20 to 60 minutes when on generator power. The 4kW load on ESS is critical, so an independant UPS after the ESS is tripped to battery when the ESS load drops, and these UPS batteries are only strong enough for about 70 seconds, so after 2 such drops I have to manually bypass the whole ESS and power the load directly from generator, so no sun power nor longer term battery backup for when the gen perhaps fails.
1) Is there no way to enable a "debug" function or similar in the Quattro or CCGX to see the exact decision being made that leads to the load drop?
2) What can I try to make this stop? I can send my .rvsc file, and the settings on my CCGX, if somebody could perhaps study it and point out flaws in the setup, or give somebody access to the live system if required.
Graph set 1
![essdropgraphs2-20220423-1353.png](/storage/attachments/32147-essdropgraphs2-20220423-1353.png)
Any help would be appreciated.