Hi
I have a 10kw Quattro does the ESS grid feed in limiter option work on the Quattro as my DNO species a max feed in of 6.5kw ???
Hi
I have a 10kw Quattro does the ESS grid feed in limiter option work on the Quattro as my DNO species a max feed in of 6.5kw ???
Yes, it will limit to whatever you set the limit to.
However keep in mind that you will get spikes to the utility when a big load is switched off of the size of that load. So if you turn off a 2kw load will exporting 6kw it will peak to 8kw for a second or 2. This normally not a problem and most utility meters won't even pick it up. Haven't had a utility complain yet.
25 People are following this question.