New install of Victron Multiplus gx trips 32A rcd, any ideas why?

I've temporally disconnected everything from the Multi apart from the mains input but when I turn the unit on it displays it's name etc then pop goes the rcd!

Multiplus-II
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·

Which RCD?

Do you have batteries connected?

0 Likes 0 ·
nick2185 avatar image nick2185 kevgermany ♦♦ commented ·
Hi.

No batteries connected - could that cause the issue?


Was making sure wiring was correct prior to connecting batteries.

Nick

0 Likes 0 ·
nick2185 avatar image nick2185 kevgermany ♦♦ commented ·
The rcd is in the consumer unit that feeds the AC-IN on the Multi.
0 Likes 0 ·
shaneyake avatar image shaneyake nick2185 commented ·
Ideally you would not have an RCD before the inverter, only on the output.
0 Likes 0 ·
nick2185 avatar image nick2185 shaneyake commented ·
Really? I thought all feeds from the CU would be protected by an rcd. I'll ask the electrician about that one.

Nick

0 Likes 0 ·
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

MultiPlus/Quattros always need a battery connected.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nick2185 avatar image nick2185 commented ·
Thank you.

Would that cause the rcd tripping issue?

Nick

0 Likes 0 ·