Can a Multiplus II 50A be used in a 30A RV?

Hello. I recently bought a Victron Multiplus II 50A, with PE, N, L1 and L2 connectors on the AC lines. However, my RV has a 30A system, with PE, N and L. Can I use the Multiplus II with such a system and wire only the L1 circuit?

Thank you.

Multiplus-II
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·

Please link to product.

0 Likes 0 ·
radubc avatar image radubc snoobler commented ·
0 Likes 0 ·
3 Answers
snoobler avatar image
snoobler answered ·

Personally, I would return that unit and get a regular Multiplus 12/3000 120V:

https://volts.ca/products/multiplus-12-3000-120-50-120v-ve-bus


If it doesn't make sense to return it, you should be able to completely ignore L2 and wire L1 to L and N to N, and it will work fine.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

radubc avatar image
radubc answered ·

Thanks for the quick reply.

I would have to send it back across Canada, and, after shipping costs, I would end up with a Multiplus for the price of Multiplus II. So I’m going to keep this one and use L1, as you said.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chuck73099 avatar image chuck73099 commented ·
We’re upgrading to a 50 amp coach next year and currently have a 30 amp coach and was wanting to do the exact same thing
0 Likes 0 ·
shaneyake avatar image
shaneyake answered ·

I would not return it.

And yes it can use used in your system with just L1 and N.

You can just limit the current to 30A in VE.Config.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.