Mppt battery amperage showing higher than battery monitor.

I noticed today that the figure from my mppt 100/50 batter amperage is significantly different (nearly 10 amps different) from that shown on the battery monitor connected to the shunt the charge controller goes through, at the time I had no significant systems drawing power, what might be causing this discrepancy ?

screenshot-20210904-135922.jpg

20210904-135728.jpg

MPPT Controllers
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Lonefox

Time to bring in the third umpire the multimeter.

0 Likes 0 ·
harmodio avatar image harmodio Alexandra ♦ commented ·

hahaha good suggestion...

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ harmodio commented ·
Also a strong possibility that there is a loose connection in the wiring somewhere. Check especially the mppt terminals
0 Likes 0 ·
3 Answers
questus avatar image
questus answered ·

moin

mit meiner Erfahrung aus 40 Jahren SY & Bootsservice bewertet:

ist ein Stromabzweig in der Verteilung das wahrscheinlichste... daraus folgt

beide Stromwerte sind ok, aber die Verdrahtung ist fehlerhaft... weil Abzweig


hol di fuchtig

Harvey

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bikerdan avatar image
bikerdan answered ·

Any more info on this? I have the exact same issue. Except mine is off by 5 amps. The charger (100/30) shows 5 more amps than the smart shunt. When there is no solar, the voltages match pretty closely. However when they are charging, the charger is showing a higher voltage too. Only about .5 volts difference though.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

questus avatar image
questus answered ·

Der BM! Monitor zeigt den SUMMEN Stromwaden-Shunts, der IST üblich zwischen MINUS Batt Pol und Abgängen, auch auf der Shunt Abgangsseite Sind sterben Verbraucher und der MPPT angeschlossen, der MPPT zeigt den am Ausgang gelieferten Strom !

daraus folgt:

1. 8,1 A fließen gen Wasserpumpe Licht usw (weil EIN geschaltet (Bild)) BM1 shunt aus Batterie

2. 9,6 A fließen tatsächlich nur in die Batterie zum Laden

das folgt logisch aus der Verklemmung am MINUS des Shunts.

ich... würde alles so verdrahtet lassen, denn die Anzeigen sind korrekt:

17,7 A werden erzeugt, davon fließen 9,6 A zur Batterie und 8,1 A werden derzeit abgenommen, alles wunderschön