Multiplus shuts down when plugged into GX

We have two Multiplus 24/5000 Master and Slave setup both Inverters are running 26xxxxx firmware, we just installed a Venus GX and as soon as we plug in the Multiplus Inverter to the GX the Inverter shuts down, we have left everything else unplugged for the purpose of diagnostics, I can see that other people have had this problem but I can't see what they have done to resolve the problem, I have tried different cables to see if I had a faulty cable, has anybody got a solution to this problem please?

MultiPlus Quattro Inverter Charger
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

"both Inverters are running 26xxxxx firmware"


The firmware version is indicated by the last 3 digits from that number.


The first four digits are designating the product ( first two digits - "26" in your case - indicate the family of products it belongs to and the next two digits designate a specific model from that family of products).


So you might or might not have the same firmware on both inverters.

0 Likes 0 ·
3 Answers
h-m-heating avatar image
h-m-heating answered ·

I updated the Firmware on the Multiplus to the latest version now the GX and Multiplus OK.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Is the Multi available in the device list on the Venus?
Have you tried to turn the Multi ON/OFF via the Venus?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

and: double check if you used the correct socket on the GX unit, if you plug it into the ethernet port it will also shut-down.

0 Likes 0 ·
h-m-heating avatar image
h-m-heating answered ·

I upgraded the Firmware and it is OK now.

2 |3000