question

lightgrid-automation avatar image
lightgrid-automation asked

Is it possible to apply peak-shaving rules to Quatros with storage - no PV.

I have 9x Quotros and 60kWh batteries. PV system is reserved for next phase. But we need to shave the peaks to lower our demand charges. Is that even possible without a PV inverter. Can the Quatros do that?
To be clear, we don't just want to self-consume at a certain level - we want to maintain a certain level (say 150kW).

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@LightGrid Automation

Yes it is, you can check the power assist function when the system is programmed and setting your input current limit to the desired level.

https://www.victronenergy.com/upload/documents/White-paper-Achieving-the-impossible-EN.pdf


2 |3000