question

greg-griffin avatar image
greg-griffin asked

Which panel voltage figure do I use when sizing voltage for panels in series?

I have some HQST 100W panels. They are 12v, but in the specs state open circuit of 24.6v and optimum operating voltage of 20.6v and operating current of 4.85a


I'm planning on connecting 7 of these in series to a 100/50 MPPT controller. Is that correct sizing? 7x12v of 7x20v?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

HI @Greg Griffin,

The PV input voltage limit for that MPPT (in your case 100V) is the absolute maximum under any conditions. So you would use the open circuit voltage (in this case 24.6V) and also take into account the temperature (PV voltage goes up when it gets colder).

So 7 in series would be too much, depending on where you live, 4 might be too much. And given there is no easily divisible for 7 panels, probably best to have 2 parallel strings of 3 panels in series.

For more precise calculations, you can use the Victron MPPT sizing calculator, that is accessible from the MPPT product page title.

2 |3000