question

halida35 avatar image
halida35 asked

Neutral-ground bonding relay on an Autotransformer

Recently I bought an Autotransformer to convert a 240vAc to 120/240VAc(split phase). This Autotransformer contains a relay to control the Ground on the neutral.

Someone know how this relay works? Needs a signal to activate?

Grounding
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

msandrew avatar image msandrew commented ·

I have this question, as well. I have a non-Victron inverter supplying 240 non-split phase to the AT. There is polarity indicated on the relay input (+ & -), so it appears to take more than a jumper. What input is required to close the circuit between output Neutral & Ground?

0 Likes 0 ·
1 Answer
Yusef Neblett avatar image
Yusef Neblett answered ·

I tested applying 24vdc and it works. If you look the big relay label inside the AT, you will find the voltage info need it.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic