should the victron mppt controller be wired directly to the battery or the negative via shunt
should the victron mppt controller be wired directly to the battery or the negative via shunt
Negative via shunt, otherwise the shunt will not know how much energy is transferred.
The shunt should be the only device that is connected to the battery (-) pole. All other chargers or consumers should be connected to the shunt. Only then the correct state of charge can be measured by the shunt.