Raspberry pi- doesn't show MPPT

'Just connected my Rasp 3B+ to my system using Venus os. That part works fine.

The BMV and MPPT are both connected with VE direct USB cables

The BMV-712 is found on Venus
The MPPT 150/60 is NOT found on Venus

I tried changing the cables but there's no difference.

Any ideas how to solve this?

Thanks

Venus OSRaspberry Pi
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·

Are they homemade or genuine Victron cables?

0 Likes 0 ·
Mike Dorsett avatar image Mike Dorsett commented ·
Is the VE direct port on the MPPT set for normal communications? If you use a laptop or other computer with Victron Connect, and the usb cable, does it show up?
0 Likes 0 ·
1 Answer
pda1 avatar image
pda1 answered ·

The solution- on the MPPT set TX to "normal communication"

That solved the immediate problem.