Is it possible to connect 2 BMV712 clocks to 1 shunt with a splitter ? The idea is to have 2 relay options?
Is it possible to connect 2 BMV712 clocks to 1 shunt with a splitter ? The idea is to have 2 relay options?
You should be able to connect 2 BMV's to one shunt directly.
The Shunt is a very low impedance source (typ 5mOhms or less), so can drive quite a few loads without loosing accuracy...
Connection of two displays to a single shunt is certainly not supported, but would be an interesting experiment!