Multiplus: Using internal 12V

I have a Multiplus 2 3000 48V. I need 12V/50mA for an external circuit. The manual says that connector J pin 1 has 12V/100mA. Normally, its purpose is an external switch. Can I use this pin as power supply and connect this to my ciruit? What should I use as ground?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
1234enough avatar image
1234enough answered ·

On multiplus-ii 5000 48, I used H main battery negative screenshot-20230902-071226-word.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image
Paul B answered ·

run a wire from G to D and use the aux relay to turn it off and on

if you use that J THEN YOU COULD DAMAGE THE INTERNAL systems so this would NOT be recommended at all

also if you use the aux relay you can turn it on and off via assistants, or even use the cerbo relay one then you can turn it on and off from the display.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1234enough avatar image
1234enough answered ·

If you use G for power, this will be at battery voltage 48v !!!!

If you use J pin 1 ensure suitable fuse below 100ma is fitted.

Good call to also use aux relay, gives options to automatically turn circuit on / off with assistant's if required.