modular fuse holder for mega-fuse

I have noticed the bolts are exposed on the bottom of the fuse holder, which I found very odd and have not seen before on any fuse holder on the market. There seems to be a shock/short hazard when mounting these fuse holders as there is not even a half millimeter between bolt and mounting surface. What do you recommend for mounting these fuse holders?

fuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

usually the fuse holder are mounted on NON metallic products, as the units are rated for less than 50 volts there is no shock hazzard, and to avoid a posiable short hazzard please mount on a non metallic surface would be my recommendation