question

trackman avatar image
trackman asked

Can a Cerbo GX control the ON/OFF/CHARGER switching of A Multiplus II ?

Can a Cerbo GX control on and off of a Multiplus? If not does anyone make a switch with 2m leads that will connect where the existing switch plugs in?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
bbmz avatar image
bbmz answered ·

Yes it can. The cerbo does not change the physical state of the switch (and therefore it is still possible to switch on the MP-IIs later - might be a safety issue) but you can disable the MP-IIs over the VE-Bus.

The control (on, off, inverter only, charger only - register 33 in VE-Bus category) obviously requires a modbus-tcp connection to your cerbo and a device that sends the „shutdown“-command.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Trackman

Yes it can. In the device list go the inverter. Top of the menu is the option to switch