python modbus - battery temperature alsways 0 degrees

Hi,

first of all: over the portal (and multiplus web app) the battery temperature is shown always correct. But the address 61 from com.victronenergy.vebus (ID 228) returns always 0.

It looks like, that all temperature values are 0. Other values, like voltages and frequencies are shown corectly.

Is there something else to do, to get the right temperature of the battery?


Bfo

batterytemperature
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Jan Novak avatar image
Jan Novak answered ·

Does someone use python to get the values from com.victronenergy.vebus:61 ?

Can you post your code or an example?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jan Novak avatar image
Jan Novak answered ·

For all of you, with the same problem:

use ID 262 of your com.victronenergy.battery to get the correct temperature and not ID61 of com.victronenergy.vebus