My setup consist of 6 X 100 A 12 V Battleborn batteries with multiplus 120/ 3000 .Color Control GX shows battery bank 100% full and battery voltage 12.5 V .Every time I get Low Baterry Alarm when I turn on 110 V appliances . Color Control GX shows Battery bank is 98 % full battery voltage drops to 11.7 and Multiplus tuns off. Any suggestions?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·
@Unal Ozbek


12.5V is not fully charged for a battle born.so the issue is your battery is low.


The excerpt below is from battle borns site.

Our charging parameters consist of the following: Bulk/absorb = 14.2 – 14.6 VFloat = 13.6 V or lower No equalization (or set it to 14.4 V) No temperature compensation Absorption time is 20 minutes per battery (if it’s an option) 12 V Bulk/absorb 14.2 – 14.6 Volts (we usually recommend 14.4) float 13.6 Volts or lower No equalization (or set it to 14.4 V), no temperature compensation and absorption time is 20-30 minutes per battery (if it’s an option).


If your parameters are correct then what ever you are using for State of Charge is not correct.

Then on top of that you will get voltage drop under load which is why the inverter is shutting down on load.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gazza avatar image
gazza answered ·

What chemistry batteries, I assume they are all in parallel? 12.5 V doesn't sound like a 100% charged battery voltage? What battery values have you programmed into the Multiplus?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Unal Ozbek avatar image Unal Ozbek commented ·
Lithium batteries 100 A 12 volt it was programmed by Battleborn
0 Likes 0 ·
gazza avatar image
gazza answered ·

These are the numbers from the Battleborn website..

Victron Energy SmartSolar MPPT charge controllers for systems equipped with solar. With Solar Charge Controllers we recommend the following settings:

  • bulk and absorption: 14.2-14.6 volts(aiming for a sweet spot of 14.4 is recommended)
  • float: 13.6

So, 12.5v is not 100% charged.