Multiplus ii 48/5000/70 disconnecting active AC input

  • Hi Guy, please help me. The multiplus ii 48/5000/70/50 keeps on disconnecting the active AC input and start inverting what could be the problem
Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
gabriel-colita avatar image
gabriel-colita answered ·

I'm leaving this answer here since I spent a lot of hours trying to figure this issue as well.

In my case, there was no issue, but if you configure ESS assistant you are forced to select a Grid Code.

Depending on your local regulation, Loss of mains detection (LOM) might be setup to only connect the grid after some minutes (for me in Romania was default to 15min).

So there was no issue, I just haven't waited enough for the invertor to allow the grid to be connected.