1x Multiplus connection to 3 phase switchboard

I am connection a ESS system and got this problem:

For the Multiplus 2 you need to keep AC In N and AC Out N separate or it will not pass ground rele test. How should Multiplus 2 be wired when you add one of those to 3 phase switchboard?

All N of the phases are connected together on the switchboard. Is there any other way to solve this than taking all the N separately on that phase that is connected to Multi?

wiring diagram
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

best practice would be to add a separate Neutral bus for the output of the Multi...