Generator size for Multiplus 24/3000

Hi there, we have a MultiPlus EasySolar inverter charger 24/3000 Mppt 150/70, wondering what size of generator is recommended. I was using our old 1kva Honda, which has now died & I think wasn't big enough as was definitely labouring. Would 2kva be big enough? Or something larger? Thanks in advance

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Anold Pande avatar image
Anold Pande answered ·

Hi ... A 2kva genset will not be big enough. You need to go bigger as u need to charge batteries and supply the loads most of the time. So you must put that into consideration. How many panels do you have on your system, how big is your battery bank and what type of batteries do u have.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

A 2kva genset will not be big enough. You need to go bigger as u need to charge batteries and supply the loads most of the time.

This kinda depends on how things are set up

A small genset purely hooked up to charge batteries? OK with no ac loads and dc charge level within genset limit.

A small genset hooked up to provide dc charge, and support small ac loads? A bit more complicated, but with ac input limit, and dc charge limit, this is achievable with a small inverter generator.

KISS.

0 Likes 0 ·