question

ruburn avatar image
ruburn asked

MPPT Charge controller sizing

If I have 6 x 330W panels (with Voc of 40.6 and Imp of 9.76) configured as 2 sets of 3 in series and both connected in parallel, what size charge controller would I need if used with a 48v battery?

My understanding is that the 3 in series would create circa 120v at 10amps but then adding the other panels in parallel would give a total of 120v at 20amps?


1647515938488.png

MPPT Controllers
1647515938488.png (18.1 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Your math's seems sound.
0 Likes 0 ·
ruburn avatar image ruburn klim8skeptic ♦ commented ·
Thanks, so I could use a 150/30 MPPT charge controller?
0 Likes 0 ·
1 Answer
klim8skeptic avatar image
klim8skeptic answered ·
Victron make a 150-35 that would be suitable.

For a few bucks more you can get a 150-45 and have a remote port and a programmable relay.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ruburn avatar image ruburn commented ·
Thanks, I'm getting my 100/30 and 150/35 controllers confused :-)
0 Likes 0 ·