Smartshunt on a standby generator starter battery?

I have a standby generator on my home which was installed by a previous homeowner. Brand is Generac, pretty common in the US. But it’s about 20 years old and doesn’t have any monitoring built in. I want to monitor the starter battery. Someone on a different discussion board suggested Smartshunt.

The Smartshunt manual refers to using the AUX connection for a starter battery. This sounds to me like an RV or boat that has a house battery and a separate starter battery. In my case, I only have a starter battery. Can I use a smartshunt with the starter battery as primary?

Yes you can use it on a starter battery as the main battery.

Hello @FrankHearble

What does the rest of your Victron world look like?

That’s perfectly fine.

Just make sure there’s only one cable between the shunt and the battery negative terminal.

The most common mistake when connecting the shunt is putting something else in between.

I don’t have any other Victron product

That isn’t necessary either; you can read the SmartShunt via Bluetooth using the Victron Connect app.

Without any other Victron equipment, a Smart Battery Sense would do as well.

I’d always leave the batteries of standby generators connected to a charger.
However, the charging voltage should be set low enough to be applied continuously.

To compare the two Victron products, you can open the demo library in the Victron Connect app.

To do this, click the three lines in the top left and select the device.

My goal is to have a battery monitor that I can integrate with my Home Assistant hub to display monitoring data. Using the smartphone app would probably have better displays, but I use Home Assistant for monitoring and controlling other devices and would prefer to have a battery monitor integrated into HA. I’ve read that HA can integrate with Victron Smartshunt by BLE.

That should indeed work that way.

The generator has an integrated trickle charger for the starter battery. It’s been dependable since we bought the home with only two failures to start. (1) When the propane fuel valve was shut off by a crew prepping our swimming pool for the winter. They turned off the supply to the pool heater not knowing it supplied the generator too. Since then, I had a plumber set up two valves downstream of the tee. (2) When the old battery could no longer hold a sufficient charge. The battery was replaced. This is why I want a monitor for battery health.

Hi Frank,

Thanks for your explanations…

I’ll just let my thoughts run freely, without sorting them.

Of course, you can monitor the battery voltage, but

a standby charger continuously charges the battery at a float voltage; there may be a little bit of electronics in there as well.

Even if the battery is worn out, the voltage will still be correct because of the charger.
In my opinion, monitoring the battery voltage in your case only has the benefit of showing whether the standby charger is working.

Whether the generator starts reliably, however, depends on whether the battery supplies enough amps during starting.

You can only check this with a load test. You did mention before that the battery had failed… That’s why regular test runs under load are required for generators.

OK, so in my case there is really no practical benefit for using the shunt. Just knowing the weekly exercise runs should be good enough. Thanks

A test run is always a good idea…

To monitor whether the charger is charging, you can also use a Smart Battery Sense. It can be read via BLE just like the other Smart devices, but is much easier to connect.

Since you were going to monitor the whole setup with Home Assistant anyway, why not just use a Shelly Plus Uni? It can measure voltage too.
Then you can avoid BLE altogether, and it should be easier to integrate into HA.