I’m considering upgrading an existing SolarEdge PV installation equipped with a three-phase (delta) inverter, a MultiPlus-II GX and Pylontech batteries to create an ESS and optimise self-consumption. Is the VM-3P75CT meter compatible with this type of network: 3 × 230 VAC, no neutral, TT earthing system? The meter’s technical documentation doesn’t include a wiring diagram for this type of network. Has anyone got any experience or a wiring diagram they could share? Would another Ethernet meter be compatible? Thanks.
Having lived in Belgium with this type of supply, 3x230 VAC without a neutral, I know exactly what you mean.
Before asking which meter would be suitable for this situation, you first need to make sure that this installation is feasible.
The Multiplus-II documentation clearly states that a three-phase delta configuration is not permitted.
I don’t know whether it’s possible to have 3 Multiplus-IIs (GX or with 3 Cerbos) operating independently of one another, connected to the same battery bank or to separate banks. An old archived topic discusses this, Three-phase 230V without neutral - to 3x single-phase 230V - Possible?, but I admit I don’t quite understand the answer in English. Perhaps you’ve already seen it?
If this installation is permitted, you’ll need 3 meters, each connected to a GX.
If you’re concerned about the meter, you must already have worked through the wiring diagram. So it would be good if you could share a diagram of what you want to install. That would make it easier for us to give you practical answers.
To clarify things for those who aren’t familiar with this situation, I came across this discussion.
Apparently, there are two possible configurations: one in star, the other in delta. That doesn’t help.
Good evening, Quentin. Thanks for your reply, but my post is in no way about a three-phase setup with 3 MultiPlus units on a delta network, as this configuration isn’t possible because no neutral is distributed. It’s about a single MultiPlus connected to 2 phases (L1 and L2, for example), and whether a main meter connected in three-phase to this type of network is compatible. It’s the same as a MultiPlus on a single-phase network. To clarify, the main question in my post is about connecting the main meter and whether its readings are valid for ESS management in a Victron architecture. Please could the community focus on this point. Thanks.
Sorry for raising the risk of incompatibility with a delta-configured three-phase installation, but with new members we sometimes get some big surprises. As always, a diagram helps make things clearer.
Indeed, if there’s only one MultiPlus-II, I don’t see a problem.
As for the meter, it seems to me that the VM-3P75CT won’t be suitable because a neutral appears to be required for this meter, as is the case with those from Carlo Gavazzi (EM24, ET340, EM540).
Have you looked at the ABB B23, which is supported by Victron? It can be wired without a neutral. However, it connects via RS485. Nothing complicated. Why do you absolutely want an Ethernet connection?
While putting together a simplified diagram, I realised that ideally there should be 2 meters, as in any installation with loads on the AC IN. The first to measure what is imported from and exported to the electricity grid. The second to measure photovoltaic generation (unless there is an alternative for receiving this data directly from the inverter).
To check: is it possible to connect 2 ABB B23 meters to the same RS485 cable and assign them different addresses? This is possible with Carlo Gavazzi products.
Thanks for the feedback and the diagram. Indeed, the ABB B23 is compatible with a 3-wire three-phase network (delta). I checked the ABB documentation, which is more comprehensive than Victron’s. The same goes for the Carlo Gavazzi EM24, as it turns out:
I prefer Ethernet because it gives you more flexibility in terms of the distance between devices. The main installation cabinet isn’t always close to the Victron equipment. An RS 485>>USB cable is therefore often a limitation or complication.
Note that Solaredge supports Modbus TCP/IP communication with the GX device, so you don’t need the meter associated with the inverter to get PV production data.
Thanks for your help, I think my issue is resolved!
I’m still curious, though, whether the VM-P75CT meter is compatible with a 3-wire setup. I’ll probably test it if no one else has tried it.
PS: What software do you use for electrical diagrams? You seem to have put that together with astonishing ease and speed.
The diagram was made with QElectroTech. It’s a bit complicated to get to grips with, but once you do, it works well.
Here’s the file sansnom.zip (16.0 KB)
As for the distance, I think I read somewhere that RS485 can go up to 1,000 m with a suitably sized cable. So that would be further than Ethernet.
Hello, I’ve been using a Victron system on a delta three-phase supply in Belgium since 2019 (single-phase on L1 and L2). It works well, but you should avoid using RS485 energy meters detected by Victron because, although they’re compatible with 3x230 V without a neutral, the Victron GX system only supports single-phase L+N or three-phase 3P+N.
As a result, power is calculated for just one phase, so all the stats are wrong. In some unfortunate cases, having AC inverters on phases L1-L2 and L2-L3, for example, causes the GX to behave and control things erratically.
I did manage to get it working, though, by connecting network-type (Ethernet) energy meters and modifying the Victron source code so that it only uses the correct data.
So it works, but not out of the box… Another option to consider: install a transformer to convert to single-phase instead of three-phase, but that costs money and means work in the distribution boards. That said, when it comes to getting the RGE installation approved with a transformer and a change to the neutral earthing arrangement, the inspection bodies are completely out of their depth and can’t approve anything, because you’re dealing with equipment used in both domestic and industrial settings, where the standards are different.
Thanks!
Hello Eric,
This is valuable feedback from your experience; thank you for sharing it.
I have a few questions about your setup:
- How is PV production communicated to the GX device?
- Which model of grid meter are you using?
- Are you running ESS with the ESS Assistant?
- Have you tried the different grid meter measurement modes on the GX device under the ESS menu: the “total of all phases” option versus the “individual phase” option? The first option should be selected.
- Is the ESS connected to L1? Otherwise, the ESS design guide specifies that functions and measurements are affected.
Thanks in advance for clarifying these points.
I also had several questions about this account of the experience.
ESS was introduced in late 2016 and has been continually improved. If the account is based on experience from 2019, it would be worth reassessing it using an up-to-date system.
My system is up to date. GX 2.33 in production; latest ESS firmware. I also use 3 ESS systems in cascade.
Carlo Gavazzi or other energy meters (currently an ET340 on the grid, 2 ET112s and 1 ET340 on the PV inverters. All these meters are RS485, but are connected to a Moxa MODBUS TCP gateway).
ESS with phase summation, inevitably.
Main system: 2 AC inverters on the INPUT of a Quattro 10k, 2 AC inverters on the OUTPUT, 2 DC inverters on Pylontech batteries (16xU3000)C. Also on site: EASYSOLAR 48/5000 and 2 Multiplus GX 48/3000 in parallel. Grid disconnection relay on the grid input.
The grid supplies me with 3x230V without a neutral. From that, I generate single-phase power with a transformer, and also three-phase power with a neutral using 3 12/1600 inverters.
So, 4 different battery packs in total; 3 systems are configured as ESS. The main one uses the grid meter, and the other two use the meter on the main GX, exposed as a Modbus service (the three-phase meters are also exposed as single-phase via a source code modification).
Yes, I’m a Victron specialist ![]()
Clearly, that’s no small residential installation you have.
Does 2.33 refer to the version of Venus OS running on your GX devices?
If so, that version dates back to 17 July 2019.
If not, I can’t see what that number refers to.
Indeed, quite a complex installation… Thanks for confirming my concerns.
I’m still perplexed, though, by the fact that the GX misinterprets the metering data when trying to ensure the ESS operates optimally. I’m no specialist; I’ve been learning about Victron for the past three months.
This evening, I was calmly rereading the ESS Design and Installation Manual and came across this FAQ:
The choice of meter, in conjunction with its own power calculation algorithm, therefore seems to affect how power readings are interpreted by the GX. The meter you mentioned (ET 340) seems to be the one that doesn’t give the best results. By contrast, an EM 24 might do the job properly.
Do you have any thoughts or experience on this?
Or perhaps it’s simply a case of testing it…
Thanks in advance.
Sorry, but if the installation is configured as three-phase, the power calculations won’t work; I’ve tried everything. The problem is that the Modbus registers read via RS485 or Ethernet (EM24) are the phase-to-neutral ones, whereas the meters provide both phase-to-phase and phase-to-neutral registers. With RS485 via USB, it’s even worse, because even if you configure the meter correctly, the GX changes the configuration itself to three-phase with neutral. We can discuss it over the phone if you like.
Hello Eric,
I’d be happy to continue our conversation over the phone. Could you email me your contact details at info@carbonconcept.be?
Thanks in advance.
Hello @Eric,
Could you send me the reference for the Moxa module you mentioned?
If I understand correctly, you reinterpret the values provided by the meter, and the Cerbo treats the values from the Moxa output as single-phase?
Are you measuring 3x230V? I ask because I can see you’re experimenting with other systems at the same time, both single-phase and three-phase 3x400V.
I’m having the same issue here: the consumption values aren’t correct once there’s feed-in, and I have two customers with the same issue. If I can find a solution, I’m interested.
So, in the end, are the values on the Cerbo correct once you’ve made your modification? Thanks in advance.
Gérard
Hello Eric, I also live in Belgium, with a 3 × 230 V delta network without a neutral, and I’ve installed a MultiPlus II (single-phase on L1 and L2).
I’m having an earthing problem: when the external AC supply is disconnected, the L2 “neutral” conductor of the AC OUT 1 output is bonded to the chassis, and I have 230 V between L1 and the chassis. Could you tell me what I should do to prevent this? Thanks in advance.
Which region are you in? I can call you if you like.