Feedback on my battery project
I’m in the home stretch of adding batteries at my place (after spending a long time looking for batteries that can be installed outside, with the MultiPlus indoors, of course). I’d like to get your opinion to make sure everything is in order.
To start with, here’s the diagram:
As for the home’s electrical circuits, nothing special: 4 circuits, 4 RCDs. One circuit will be rewired to bring together the whole “critical load” section (maximum consumption of 500W, and more like 250W nominally).
On the solar side, there are 16 375Wc panels with Enphase iq7a microinverters, split into 2 arrays, one with 10 panels and the other with 6. I know I’m a bit close to the limit in terms of battery capacity, but it should normally be enough for the output of the 10 solar panels, so it should be fine.
For the battery setup, there will be:
The circuit breakers/RCDs are all shown on the plan. For the cable cross-sections, we’ll use 10mm2 for the MultiPlus (AC IN and AC OUT) and 25mm2 35mm2 to the battery.
Overall, I think everything is in order (but I’m far from an expert in this area), though I have a few questions:
  • The Enphase gateway uses PLC to communicate with the microinverters. Will the PLC signal pass between AC IN and AC OUT? I think so, as they are directly coupled (in normal mode, of course; in off-grid mode it’s a different matter). => Potential stumbling block: I’m not sure the MultiPlus lets the PLC signal pass between AC OUT and AC IN.
  • I’ve seen quite a few discussions about earthing arrangements, and I have to admit I’m a bit lost. Is there anything in particular I should know? => Nothing special
  • On the Enphase side, I’ve enabled the Modbus protocol on the gateway (Enphase did this themselves when I told them I was going to install Victron), but I’m not really sure what it’s for. It isn’t used for AC coupling with Victron (frequency shifting), so I’m not really sure… That’s fine; it’s just used to send information to Victron so that everything is in one place.
Thanks in advance for your feedback.
There are several points about this installation that concern me.
  • Positioning the AC-coupled PV generation after the normal and critical loads creates a risk of overcurrent. This is a frequently observed error in older installations.
  • The circuit breaker at the Multiplus-II input must not be downstream of the house’s RCD but connected directly to the grid.
  • The suggested battery is not powerful enough for the Multiplus-II 5kVA. It would be fine for a 3kVA unit.
  • Use 35mm² battery cabling for a 3kVA unit and 70mm² for a 5kVA unit.
Ideally, the protection for energy sources should be separated from that for consumers by installing an interconnection panel that brings the sources together and feeds the consumers. This is much neater than integrating everything into the main panel. Ideally, the AC-coupled PV generation should also have its own panel, connected to the energy-source interconnection panel.
Sharing the PV generation array between AC IN and AC OUT with a single gateway is not documented. In my experience, PLC for a computer network does not pass through the Multiplus-II. I don’t know why, or whether this is normal. The real experts might be able to answer that.
Sharing the PV generation array means doubling up on the surge protectors and RCDs for the PV systems, which adds extra cost. It also creates a problem with where to place the PV generation sensor.
There may be solutions to all this, but in my view, if the installation is already operational, it would be best to keep the PV generation on the AC IN side (I’m assuming it is, since the IQ7A units are older models). If this is a new installation, the best option would be to split the PV generation between an AC-coupled array and a DC-coupled array, but this involves a lot of extra cost without any real return on investment.
Enabling Modbus TCP on the Enphase gateway makes it possible to integrate the gateway with the GX, allowing it to monitor PV generation. However, it is not ideal for controlling exports because of the lack of responsiveness. (See Feedback on Enphase integration via Modbus TCP). This has nothing to do with frequency shifting (frequency shifting).
Sharing the PV generation array also creates a problem when integrating the gateway, which can only be assigned to one side or the other of the Multiplus-II. Once again, there are solutions, but they would entail additional costs.
The essential grid meter is missing for ESS to work properly when loads are on both sides of the Multiplus-II. The external sensor works, but is not recommended in this situation.
Thanks for your feedback, I’ve updated the diagram:
However, I have a few questions:
The suggested battery is not powerful enough for the MultiPlus-II 5kVA. It would be fine for a 3kVA.
According to the documentation, the 5000 needs between 200 Ah and 800 Ah. With 10kwh, that gives 200 Ah, so I thought I’d be OK.
35mm² battery cabling for a 3kVA, 70mm² for a 5kVA.
That’s one of my concerns. If you look at Pylontech, it has to be 25mm2, and the battery manufacturer also supplies 25mm2 cables. But you’re right, that does seem a bit marginal. The Victron draws 70A, the battery 100A. According to the Victron table, I’d need at least 35, and 50 would be better:
Sharing the PV generation system between AC IN and AC OUT with a single gateway is not documented. In my experience, powerline communication for a computer network doesn’t pass through the MultiPlus-II. I don’t know why, or whether that’s normal. The experts might be able to shed some light on this.
That, on the other hand, is a problem. I can’t put all my PV on the MultiPlus (I have 6kwc, so the 5kVA wouldn’t comply with the 1.0 factor rule), hence my idea of separating them. But if the powerline signal no longer gets through, the Enphase gateway won’t see all the microinverters, which is an issue.
Sharing the PV generation system also means doubling up on the surge protectors and RCDs for the PV systems, so there’s an additional cost. It also creates a problem with where to place the PV generation sensor.
That’s true about the surge protectors; I’ll need a new one. I have a PV panel, so there’s no problem there—I’ve got plenty of space in it. As for the generation sensor, it won’t change much: it’s directly on the PV feed and therefore picks up two cables (one from each PV array).
There may be solutions to all this, but the best option, in my view, would be to keep the PV generation on the AC IN side if the system is already up and running (I’m assuming it is, since the IQ7A are older models). If this is a new installation, then ideally the PV generation should be split between an AC-coupled system and a DC-coupled system, but that involves a lot of extra cost without any real return.
Yes, the installation is already done, but in the event of a major outage I wanted to be able to restart generation. Even if I keep 30% of the batteries (around 3kWh), that will only last 10/12 hours. With a PV array, I’d have a chance of lasting longer.
Sharing the PV generation system also creates a problem when integrating the gateway, which can only be assigned to one side or the other of the MultiPlus-II. Once again, there are solutions, but they would involve additional costs.
Oh, that’s a pain too. I thought you could have one PV array on AC IN and one on AC OUT. After all, the MultiPlus only needs to manage the AC IN PV array in backup mode.
The grid meter, which is essential for ESS to work properly when the loads are on both sides of the MultiPlus-II, is missing. The external sensor works, but isn’t recommended in this case.
I specifically wanted to use the external sensor, which avoids having to make more connections and therefore avoids the risks of loose connections or problems throughout the house if the meter dies. Why is that a problem?
Thanks very much for your feedback.
Regarding the battery, its storage capacity is sufficient. But the current—and consequently its power—are insufficient. According to the specifications, it supports a maximum of 100A for charging and discharging, and its service life is calculated at a current of 50A. These figures are well below what a 5kVA unit can draw.
You’re right that the charging current is limited to 70A. However, the discharge current can reach 200A peak and 140A for several minutes (6500VA output).
At 140A, theoretically, you damage the cells if the BMS doesn’t prevent energy from being drawn from the battery. In short, the battery will tend to limit the performance of the Multiplus-II 5kVA in order to stay within the stated CCL and DCL. It’s much better suited to a 3kVA unit.
With this type of battery, you’d need at least two in parallel for it to work properly.
As for the 35 or 70mm² cable, that’s the section running from the circuit breaker (or knife switch disconnector) to the Multiplus-II. The Pylontech cable (or similar) is a special type that pushes the limits a little. It’s rated for a maximum of 100A continuous and 125A peak (for less than 15s).
You probably understand better now.
As for the issue related to PLC, this would need to be confirmed by other members or technicians. I only told you about an experience that wasn’t conclusive.
In mainland France, subscribers are entitled to compensation if the power is out for more than 5 hours. Enedis has every incentive to restore power within 5 hours. Even so, natural disasters sometimes interrupt the electricity supply for more than 5 hours. Every year, some subscribers are affected by this. DC coupling is better for protecting against very long outages, since AC-coupled PV generation won’t restart when the batteries are empty because the Multiplus-II will be shut down. Don’t forget that detail.
Integrating PV generation into the GX isn’t essential for ESS to work. Still, it’s a good thing to do for a properly finished installation. The same goes for the external sensor, which prevents you from distinguishing between loads on the input and the output: it doesn’t stop ESS from working, but you lose information and the feature that lets you use the batteries only for the consumption of critical loads. Few people choose it.
I doubt the meter will fail before the Multiplus-II. That would indicate a fault. As for the connections, they all carry the same risk. There’s no reason to worry about one more connection.
When you’re investing several thousand euros, why skimp on details that won’t even account for 3% of the final bill?
OK, thanks for the feedback. So indeed, for my battery, it’ll be the 3000VA model with a 35mm2 cable.
Integrating PV production into the GX isn’t essential for ESS to work. It’s still a good thing to do for a properly finished installation. Just like the external sensor, which means you can’t distinguish between the loads on the input and output, it doesn’t stop ESS from working, but you lose information and the feature that lets you use the batteries only for the consumption of critical loads. Few people choose it.
Basically, if I put the external current sensor on the EDF supply, will the Multiplus no longer know how much ACOUT1 is consuming?
I doubt the meter will fail before the Multiplus-II. That would be a sign of a fault. As far as the connections are concerned, they all carry the same risk. There’s no reason to worry about one additional connection.
Put like that, you’re right, I might as well install the meter.
As for powerline communication, that would indeed be a deal-breaker for my project… I’ll wait to hear back from someone else.
When you install the external current sensor, all the loads and PV generation are seen as being connected to the output of the Multiplus-II. The Multiplus-II assumes there is nothing connected to the input.
By reducing the Multiplus-II’s power to 3 kVA, you can’t connect the array of 10 panels and IQ7A microinverters to its output, but you can connect the array of 6.
Yes, yes, of course, I’d connect the 6-panel array to the 3000VA.
But anyway, if the powerline communication doesn’t work and, on top of that, the Victron can’t have panels on ACIN and ACOUT at the same time, that rather calls my project into question.
You can have PV panels on both sides. However, integrating the gateway via Modbus TCP will only let you report your production on one side or the other. If you choose the external sensor option, they’ll be on the output anyway because, by definition, there’s nothing on the input with this option.
The question of powerline communication is a determining factor in your current project.
OK, so I’ll definitely need an extra meter to keep everything properly separated. Would the Victron Energy VM-3P75CT Energy Meter work?
I’ll wait for more feedback on powerline communications, because yes, it would make the whole project fail if it didn’t work.
With a Multiplus-II GX, you only have a BMS-Can port and no VE.Can port. You won’t be able to connect the VM-3P75CT meter via VE.Can. You’ll have to connect it via Ethernet. Communication will depend on the IT network. A failure, update or restart of the IT network components will cause ESS to malfunction. Nothing serious, but there are other meters that won’t have this drawback.
Personally, I prefer the grid meter to be connected directly to the GX, for example via RS485 using a USB adapter, such as the ET112 meter.
Okay, thanks for the feedback. However, there’s still something I don’t understand: in normal mode, as far as I’m concerned, the MultiPlus just needs to know whether I’m exporting power to the grid (EDF) or drawing power from it, and from there, in ESS mode, it’ll decide whether to charge or discharge.
It doesn’t need to know about solar production or consumption
on ACOUT/IN.
In backup mode, it needs to know how much the solar panels are producing in order to regulate their output, but it can find that out by monitoring its ACIN.
So just a current clamp on the incoming EDF supply should be enough for it to work, and that’s exactly what the external current sensor allows you to do.
Sorry, but I’m really struggling to understand what an ET112 would actually do for me.
These are subtleties. As I was saying, with the external sensor, it works, but…
Furthermore, a meter is more accurate than the external sensor. It continues to count even if the GX is disconnected.
Ultimately, this is the recommendation made by Victron and stated in the documentation.
The use of the external sensor is not mentioned in the ESS documentation. However, it works with known limitations. Older official presentations included this scenario, but it is no longer the current recommendation.
A PV production meter (whether physical, integrated via Modbus-TCP or virtual and powered by Node-RED) is not mandatory. It is a useful way to get an overview of the installation in VRM. Even in offline mode, it is not mandatory. Regulation is based on frequency alone.
Hi, thanks for getting back to me. One quick bonus question: do you need to put a surge protector on the AC output? I’ve seen some people install one, and it seems like a sensible idea to me for backup mode.
The idea behind this is to try to pass the purple Consuel inspection (well, that’s what I’m hoping for).
Hi Quentin, it doesn’t seem straightforward to carry out your project. I’m also starting with an installation using microinverters, but I’m removing them to switch to DC coupling with 2 strings on one MPPT. It’s easier to manage the battery that way, and the effective storage efficiency is higher. A friend with the same setup as you, who wanted to stay AC-coupled, had to switch to a Quattro because it has two AC inputs. I’m also installing a meter and a Cerbo GX; the whole setup will comply with the new NF C 15-100 standard, which has been mandatory since September 2025. MultiPlus 5000 70/50 and a 16 kWh DIY battery. But I wouldn’t want to have to carry out your project. I think I’d simplify things by installing a DC array with an MPPT; otherwise, you could go with the Quattro, but you won’t get the same storage performance because of the conversion losses: DC to AC, then AC to DC, then DC to AC for the loads. On top of that, the Victron MPPT can optimise battery charging independently of the MultiPlus (with the right settings). So, as already mentioned, it’s useful in the event of a prolonged grid outage. Good luck!
Thanks, Yvon. A small correction: It’s not my project, but @zoic21’s.
In a way, you confirm what I was saying. It’s preferable to have one field with AC coupling and another with DC coupling. This solves all the problems.
Oops, Quentin, I mixed you up with someone else. I do prefer it, actually, because I know it better, having done it on vans. After that, I was wondering about the efficiencies and shading, which favour microinverters in AC coupling for self-consumption and selling surplus back to the grid: 97% with Enphase, versus 94% with Victron MPPT and MultiPlus, according to my sources. For use after battery storage, efficiency favours DC coupling of the panels (74 vs 82%). The choice depends on which way the balance tips between solar power, self-consumption and storage.
Good evening
Thanks for the feedback. I think that initially I’ll leave the panels on the AC-in side and, indeed, perhaps switch to DC mode with 6 panels instead (but that’s a pain—it means getting a professional in…)
However, I still have a few questions about the wiring:
  • Do I need a surge arrester on the AC-out1 side?
  • I understand that you shouldn’t have a 30 mA RCD on the AC-in, but I still find that a bit hard to get my head around. An RCD is there to protect people from current leakage, particularly on metal equipment, which is the case with the MultiPlus itself… So isn’t there a risk if something goes wrong and you touch the MultiPlus?
  • Regarding the type of RCD for the AC-out, Type AC or Type A? If one is needed on the AC-in, which type?
  • I’ve seen diagrams with a 125 A circuit breaker on the DC side between the batteries and the MultiPlus, as well as a knife switch. Do you really need both? Or is the 125 A circuit breaker enough?
  • I’ve read that you shouldn’t earth the batteries, but I see lots of diagrams where the Pylontech batteries are earthed… Even though I’m not planning to use Pylontech, I think there’s an earth terminal on the batteries. What should I do?
I want to make sure I have a safe installation and perhaps get it inspected by Consuel (although, from what I’ve read, there’s some room for interpretation on that, as far as I understand).
Thanks in advance for your reply.
You don’t need a surge arrester on the output of the MultiPlus-II. However, you do need one on the PV generation side, regardless of which side of the MultiPlus-II it is on. The surge arrester should be placed as close as possible to where lightning could enter. If the cables between the panels are long, you need to install one in each panel.
The MultiPlus-II is considered a technical component. It doesn’t require an RCD intended to protect people. Your question about people touching the device is a valid one. Could a technician explain whether there is any risk in this regard?
The RCDs connected to the output of the MultiPlus-II depend on the consumer circuits they protect. They have nothing to do with the presence of the MultiPlus-II.
Circuit breakers or knife switches are overcurrent protection devices. Each cable has a maximum permissible current, which depends on its cross-section and length. Every cable must be protected to ensure that the maximum permissible current is never exceeded. The total number of protection devices depends on the installation and the level of protection you want. There is no reason to install two devices one after another. However, in the case of a busbar (such as the Lynx), each connection leading to the busbar must be protected. This can give the impression that there are two devices in succession.
You can earth the batteries, but that changes the earthing arrangement. If you earth the batteries (the negative terminal), additional safety equipment is required, which is expensive. It is permissible not to connect the batteries to earth because they are low voltage (DC below 120 V) (SELV). However, you must make sure there is no connection anywhere between a polarity (the negative terminal) and earth. For example, neither polarity of a vehicle is connected to earth. It would be difficult to drive with a cable permanently connecting the vehicle to earth. Everyone touches the bodywork, even though it is connected to the battery negative, without worrying about 12 or 24 V.
Obtaining Consuel approval can be complicated because there are many details to comply with. They don’t all pose the same level of risk. You can have a safe installation that isn’t approved because of something as simple as a missing label. In any case, making the effort to comply with the standards is certainly the right place to start. After that, it’s up to you whether to pay a little over €200 for an authorised technician to approve your installation. Without approval, your home insurance will refuse to cover damage caused by your installation. So, if you pay for home insurance and want to be covered in the event of damage caused by your installation, it must be approved, and therefore compliant.
I invite you to read Pierre’s account of his experience getting his installation approved.