Hello,
I’m in the home stretch of adding batteries at my place (after spending a long time looking for batteries that can be installed outside, with the MultiPlus indoors, of course). I’d like to get your opinion to make sure everything is in order.
To start with, here’s the diagram:
As for the home’s electrical circuits, nothing special: 4 circuits, 4 RCDs. One circuit will be rewired to bring together the whole “critical load” section (maximum consumption of 500W, and more like 250W nominally).
On the solar side, there are 16 375Wc panels with Enphase iq7a microinverters, split into 2 arrays, one with 10 panels and the other with 6. I know I’m a bit close to the limit in terms of battery capacity, but it should normally be enough for the output of the 10 solar panels, so it should be fine.
For the battery setup, there will be:
- one MultiPlus II GX
5000VA3000VA - one 10.24kWh battery (probably this one: https://www.nkon.nl/en/nkon-ess-pro-51-2v-10kwh-thuisbatterij.html
The circuit breakers/RCDs are all shown on the plan. For the cable cross-sections, we’ll use 10mm2 for the MultiPlus (AC IN and AC OUT) and 25mm2 35mm2 to the battery.
Overall, I think everything is in order (but I’m far from an expert in this area), though I have a few questions:
- The Enphase gateway uses PLC to communicate with the microinverters. Will the PLC signal pass between AC IN and AC OUT? I think so, as they are directly coupled (in normal mode, of course; in off-grid mode it’s a different matter). => Potential stumbling block: I’m not sure the MultiPlus lets the PLC signal pass between AC OUT and AC IN.
I’ve seen quite a few discussions about earthing arrangements, and I have to admit I’m a bit lost. Is there anything in particular I should know?=> Nothing specialOn the Enphase side, I’ve enabled the Modbus protocol on the gateway (Enphase did this themselves when I told them I was going to install Victron), but I’m not really sure what it’s for. It isn’t used for AC coupling with Victron (frequency shifting), so I’m not really sure…That’s fine; it’s just used to send information to Victron so that everything is in one place.
Thanks in advance for your feedback.