overthehill asked

2 Orion Tr smart DC to DC chargers running in parallel.

I'm looking at setting up 2 Orion Tr smart DC to DC chargers running off of an alternator and solar with a MMPT BlueSolar charge controller. How does the system know not to overcharge the batteries. How does it synchronize the charging profiles of the 3 devices?

orion-tr smart
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
d-winterburn avatar image
d-winterburn answered ·

If the charge profiles are all identical you shouldn't have any problems at all. Bulk, Absorption, Float, Compensation...everything must be exactly the same. Charge current is a function of the SOC of the battery so there is no chance of overcharging if the parameters are set correctly for your particular battery type.