Hello. I have a MultiPlus-II 3000 inverter + Raspberry Pi 3 (Venus OS) for control + MK3-USB.
I want to charge the batteries at a specific time (for example, only at night when I have cheap electricity), as well as discharge in the evening in the network when electricity is expensive. I experimented with manually controlling ESS-> GridSetpoint, but would like to do it automatically. Is such functionality already implemented? If not, tell me how I can implement it?

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
markus avatar image
markus answered ·

Hi,

you could use Modbus TCP to set the Grid Setpoint from a PLC or some other control computer.

See here: https://www.victronenergy.com/live/ccgx:modbustcp_faq

Grid power setpoint - Modbus-TCP register 2700

Positive: take power from grid. Negative: send power to grid.

Default: 30 W.

This register has range -32768W to 32767W (scale factor=1). Use register 2703 for a larger range (scale factor=0.01).

Best Regards,

Markus


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

Yes, we have done this before with Control4 home automation with a ModbusTCP driver to write to the registers - in our case 2703 because it was a large system.

0 Likes 0 ·
martijnt avatar image martijnt commented ·
I've tried using this and for some reason, I cannot get it to accept negative values. Setting it to a positive value works, when running a debug output (Node-RED) I see the value change over time to the new value, but negative values: nothing.


Any clue?


0 Likes 0 ·
martijnt avatar image martijnt martijnt commented ·
After much searching, it seems you have to set it to 65536 + (your negative value), so -500 would be 65036. Weird.
0 Likes 0 ·
rnr102 avatar image
rnr102 answered ·

Thank you very much.
I managed to understand the Modbus-TCP protocol.
In my case it was 37 register. I can change the value manually using the Modbus Poll program.
Now I will think about further implementation.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Meine_Energiewende avatar image
Meine_Energiewende answered ·

You can also set the grid setpoint via MQTT.

Jens