Can't Zero a BMV600S

Hello,

I have a BMV600S that reads -1.5A when there is no current flowing through the shunt, as verified by two ammeters. I have tried the Zeroing procedure but it makes no difference. I understand that I should select Zero in the setup, then press the setup button for 3 seconds and I should get a response saying "ok". I don't get the "ok", it just goes straight out of setup. Any ideas?

Thanks,

Aedan

BMV Battery Monitor
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
aedanc avatar image
aedanc answered ·

Thank you very much Daniel, that worked perfectly. I promise I'll read the manual more carefully next time!

Aedan

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @AedanC

I think you have to press the 'select' button, not the 'setup' button.