15KVA quattro with 30kWh of BYD

2 x 150/100 MPPTs

3 x 10kWh Byd Bbox

Full sunshine today and client batteries only went up to 72%

This system is capable of producing 50kWh in a day. Please give advise as too issue.

BYD
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
BYD_service avatar image

Hello,

In order to evaluate if there is an issue it is necessary to confirm if the MPPT haven't charged the batteries whilst there was excess of PV generation. And if that's the case please check in the history of the system (you can download this from VRM) what was the CCL at the time. This will tell you which of the devices decided no to charge the battery