3x Quattro 48/10000 Grid 250A peakshaving
Dear community,
I would like to pass this trough the community about the ESS system.
i want to use the inverters for peak shaving parrallel to the grid. Because the grid connection is 250A and the quattro would not handle that :D.
I would like to use the quattro as a bidirectional inverter.
is it still possible to reach the 319A peak or only the 284 for continues in total?
With kind regard,
Marc
ESSquattro 10kvapeak shaving
1 comment
2 |3000
marc-heide avatar image marc-heide commented ·
I am just wondering if it reacts fast enough with high peaks.
0 Likes 0 ·
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·
As long as you have a grid connection each Quattro will only deliver it's max. continuous power, around 8000W at 25°C.
It also needs a few seconds to ramp up the power, short spikes (starting a big motor or something like that) are always coming from the grid.
1 comment
2 |3000
Thanks for the information. It is verry helpfull to me.
0 Likes 0 ·