question

pedaaa avatar image
pedaaa asked

Modbus Register for CCL (Charge Current Limit) from BMS?

Hello, i am searching for the CCL-value that my BMS is sending to Victron:

i can see this limit in remote console device-> battery -> parameters:

1673617874971.png


in this case its 30A, because the BMS is currently sending a lower limit.


But on Modbus, i can only find the CCL that i have manually set in DVCC:

This can be found via Register 2705:

1673617951147.png


So i can only read the manual CCL-setting (register 2705) -> 100A

but not the actual CCL, victron is using as the limit -> BMS-CCL -> 30A


Are there any ideas how to read this BMS CCL??

Is there a hidden Modbus Register for that?


Modbus TCP
1673617874971.png (41.0 KiB)
1673617951147.png (32.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
The CAN registers for these aren't public, so I would presume this isn't either.

I had to do some googling and can-sniffing to find the relevant registers.

0 Likes 0 ·
1 Answer
wkirby avatar image
wkirby answered ·

Use register 308.
1673620512514.png


1673620512514.png (13.2 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pedaaa avatar image pedaaa commented ·

aahhhh its register 307...

i feel stupid now... Could have find it myself in the Modbus-List.


thanks you!


0 Likes 0 ·
wkirby avatar image wkirby ♦♦ pedaaa commented ·
Oh yes, sorry, 307 not 308.
0 Likes 0 ·