12 x Pylontech US3000C

Heya,

I understood from different answers here that one can connect 12 x Pylontech US3000C without using a LV-Hub. Does anyone has a schema on how to do it? Or even better pictures with a system with 12 batteries (or more) without LV-Hub.


Thank you

Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
wkirby avatar image
wkirby answered ·

Up to 16x US3000C modules can be connected in one battery group without an LV-HUB.
Arrange your DC cabling according to how much current your installation will use or charge.
Consult the US3000C manuals for more details regarding the wiring specific to your particular installation.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mariusv avatar image mariusv commented ·
Thank you very much. Just to make sure I understand correctly. Will they be two packs of 8 or all 16 in one pack but with multiple positive and negatives tight to the busbar ?



0 Likes 0 ·
Alexandra avatar image Alexandra ♦ mariusv commented ·

Datawise they are stacked in 16.


Physical stacking is recommended as in 4s. You can have the cabinet and ither methods change that.

Electrically is what the cables can handle and good current sharing methods. And yes positive and negative take offs not off same battery.

Pylontec show the set up in the manual. Although i dont totally agree with it

0 Likes 0 ·
yann avatar image
yann answered ·

Here is one of my pylontech systems

Here there is only 8 US3000, but the logic is the same if you add more.

You can see two RJ45 sockets on the side of the racks, under the power connectors : one is for the CAN link to the GX device, the other one for the last battery "link port 1" to the "link port 0" of the first one on the next rack.


img-20221016-102140-845.jpg


img-20221016-102505-397.jpg



img-20221016-102657-719.jpgconnections inside the rack

img-20221019-103414-106.jpgPower connections and CAN cable to the main DC panel


img-20221019-115325-454.jpg


img-20221019-133234-517.jpg

img-20221019-133441-558.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image
wkirby answered ·

@Yann That a nice way to do it.

This is my variation using a 1U feed through panel. You could place more than one feed through panel or fir more Radsok connectors on the one feed through panel to increase the current carrying capacity if needed. It works rather well.

1667895581814.png



1667895581814.png (1.2 MiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

yann avatar image yann commented ·

@WKirby

Nice setup !


There is no problem with batteries touching each other ? I thought there's a need for air circulation between each one. I'm pretty sure I read this somewhere on pylontech's documentation.


0 Likes 0 ·
hominidae avatar image hominidae yann commented ·

I have 6 of these in a 42HE open Rack, but put them in tight.

Temps between modules differ 2-3 degC when in Use.

...as the standard Pylontech Rack comes in 24HE, named to be suitable for 12xUS2000C or 8xUS3000C I made that mistake (24HE = 8x3HE US3000C).

I will soon re-arrange the units to leave some more room. During Winter, they are still safe, even generate a better climate to reach the standard 25degC.

0 Likes 0 ·
mariusv avatar image mariusv yann commented ·

@WKirby

WoW, awesome setup!

What is the thing on top which gets all the earthing, can and power in it?

I just added few more batteries to my setup but because in the rack I can't fit more than 8 x US3000C I have two outside of the rack but seems like I can't add them to the other 8 because of too short of the plus/minus cable and same for comms. Any idea?


0 Likes 0 ·