Baterist byd LVL can not charge and discharge.

Hello everyone, we have established a system in turkey. In the system, there are 3 units of quatro 48/15000 in each phase, also mppt charge 150/85 x 6 units, Fronius eco 27, symo 20 and symo 10 available, lastly BYD LVL 15.4 kWh x 10 units available. all installations in the system are ok, but the batteries are not charging and discharging. Although the battery status shows 49% on the screen, the charge does not show any current, but it reads the voltage. I'm looking for help on this matter.

BYD
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @veliozbek,

Starting with the basic troubleshooting,

Can you please check the voltage at the battery connection terminals of the Quattros and the battery connection terminals of the BYD battery and make sure that they are reading the same?

11 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

veliozbek avatar image veliozbek commented ·

hello guy first of all thanks for your help. There will be an opportunity to review this project for our project in two weeks. If there are a few answers to the questions you asked, what should we do? can you inform me about this. Finally, do we have a chance to get help by connecting to you live? thanks

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ veliozbek commented ·
@veliozbek

Does the LVL use BMU?

We had a system with Flex Lites doing something similar. Reporting no current movement (with a clamp meter there is current moving in and out).

A total system restart worked to clear the issue.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ veliozbek commented ·
Hi @veliozbek,

The best way to get live 1:1 support is to contact your Victron Dealer or Victron regional sales manager - in many regions there are specialist technicians who make themselves available for this level of support.


0 Likes 0 ·
veliozbek avatar image veliozbek Guy Stewart (Victron Community Manager) ♦♦ commented ·

hello steward, this project is the largest domestic storage and ESS project in Turkey, and the owner of both the application site and the facility is a very important business person in Turkey. But unfortunately we can't get enough support for this project in victron turkey. What should we do if the voltage at the Quattros battery connection terminal and the connection terminal voltage of the BYD battery are the same or different in the first reply you wrote to us on this subject. In addition, we will make 6 of this project according to the performance of the current project. That's why it's very important to us. Thank you

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ veliozbek commented ·
Hi @veliozbek,

I understand, I have got in touch with Islam Varol the sales manager for that region to see if there is anything that can be done from our end.


0 Likes 0 ·
veliozbek avatar image veliozbek Guy Stewart (Victron Community Manager) ♦♦ commented ·


cf8ff2cb-edb5-4e61-a148-1d69e742350a.jpeg

bu linke yorumunuz nedir

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ veliozbek commented ·

Why is there a lynx shunt 1000 installed in this system? It should not be necessary with the BYD BMU. It needs to have a fuse installed that does not come supplied, perhaps it wasn't installed? Double check it.

cleanshot-2022-08-04-at-175350.jpg


Remove the covers of the lynx distributors;

Isolate(disconnect) the AC grid connection to the Multis, and the PV input connection to the MPPTs, make sure the BYD battery is on.

Using a multimeter - measure and record what is the measured voltage is on;

  1. the BYD Battery terminals for each battery
  2. between the bus bars underneath the lynx distributor covers on the left hand side
  3. between the bus bars underneath the lynx distributor covers on the right hand side
  4. between the external bus bars connecting the lynx distributors together
  5. on the battery terminal connection points for each of the three Quattros.
  6. on the battery terminal connection screws of the MPPTs

If there is any variation between any of those figures, VRM is reporting that there is, so you need to try to identify why.

If it is not obvious, take lots of photos and report back and maybe we can see something.

0 Likes 0 ·
veliozbek avatar image veliozbek Guy Stewart (Victron Community Manager) ♦♦ commented ·

Merhaba @Guy Stewart (Victron Community Manager) , yardımlarınız için tekrar teşekkürler. Mevcut busbar sistemiyle baralarla birlikte. Ancak BYD pil girişine izin vermiyor. Aslında tek pil ile denedik bugün tekrar bakacağız. ikia öneriyor. BYD ve Victron arasında minimum bir yapılandırma var mı? ya da tüm pil gruplarını birbirine bağlamalı ve gelecekte olacakları için zaman vermeliyiz.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ veliozbek commented ·
Can you post the measurements for 1 to 6 that you wrote down here?


Analysis of those voltages measured at those locations is the next step in the troubleshooting process.

0 Likes 0 ·
veliozbek avatar image veliozbek Guy Stewart (Victron Community Manager) ♦♦ commented ·

hello, today we separated the whole system from each other. we removed all the ends of the batteries connected to the busbars. and batteries each left alone. We also canceled the communication cables with each other. Then we measured the outputs to the busbars behind the battery separately from each battery, but we could not see even 1 V at the output of any of them.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ veliozbek commented ·

What I would have done to troubleshoot the system was wire it together as described by the documentation and training, and then take voltage measurements at the points I listed 1 to 6 above. That would point to where the issue is.

Did you record the voltage readings at each of the points as I described above?

Did you confirm that the fuse was installed on the lynx shunt? Did you find out from the installer why the lynx shunt is installed in the system at all?

This would all be best discussed directly with your Victron distributor network and regional sales manager - they are the best line of support.

0 Likes 0 ·
Rob Fijn avatar image
Rob Fijn answered ·

Hello Veliozbek, in the device list of the Cerbo, do you see the BYD batteries ?

If yes, then go in to this menu and go to details. Here you must see some more about all your batteries.

I am interested to know what you find.

Rob

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

veliozbek avatar image
veliozbek answered ·

hello guy first of all thanks for your help. There will be an opportunity to review this project for our project in two weeks. If there are a few answers to the questions you asked, what should we do? can you inform me about this. Finally, do we have a chance to get help by connecting to you live? thanks

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Fijn avatar image
Rob Fijn answered ·

Hello Veliozbek, The Cerbo GX must be able to 'see' the BYD batteries. Remember the special type-A cable between the BYD and the Cerbo. Bring the BYD app on you phone and make sure it is updated. All communication between the batteries must be good.

With this you must be able to get this going.

Rob

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ertaco avatar image
ertaco answered ·

Hello @Guy Stewart (Victron Community Manager) thank you for your help! to our installer @veliozbek...


In this project, we have 10x BYD LVL 15,4 kWh which are already comissioned and updated, the status in the battery BMU shows normal, the led status is on standby without any charge or discharge.


The inverters or MPPT devices dont charge the batteries and we have the screen on cerbo gx as below; no SOC info or current flow indicated.


Do you think the root cause still occured by the BYD batteries or the DC busbars and fuses? Or something missing on Victron configuration? If you have experienced before.

Thank you.