samsolar avatar image
samsolar asked
Cerbo GX detecting 5 out of 6 Pylontech batteries?
Hi All
I have a problem getting my 6 Pylontech batteries to show up when connected to a Cerbo GX.
The batteries are a mixture as follows:
  • 2 x US2000C
  • 4 x US2000
These are all linked together via the link ports as per Pylontech manual (link port 1 on first battery going to link port 0 on second etc), and I believe this is correct as I have used the same array previously on another inverter.
The batteries are connected to the BMS-Can port of a Cerbo GX using a VE.Can to CAN-bus BMS type A cable, and to the CAN port of the master battery.
After connecting the batteries and booting up the Cerbo for the first time, the Pylontech battery device was recognised straight away - looking promising:
However the Cerbo only shows 5 batteries are connected, not 6:
In addition the installed capacity shows as 250Ah, but I'd expect it to be 300Ah (6 x 50). Charge limits seem to be similarly reduced. It's like the 6th battery is simply not being detected?
When I look at the batteries themselves they are all getting charged/discharged together and are staying balanced.
Things I have tried...
  • Removing each battery individually from the array. This did not make a difference. As soon as any of the batteries are removed, the Cerbo reports that there are now only 4! And removing 2 batteries then shows that only 3 are connected etc.
  • Reordered the batteries so the two US2000C are not together - e.g. US2000C > US2000 > US2000 > US2000C > US2000 > US2000. This failed to start up so I put the two US2000C back in front.
I'm not sure what I'm doing wrong, but if anyone can help or I'd greatly appreciate it.
Thanks
Sam
Pylontech
samsolar answered ·
Thanks for your answer lifeingalicia.
I've now solved the problem, and embarrassingly it was because I was using the wrong link cables to link the pylontech's together!
For info, I have 3 x stacks of 2 x batteries (vertically mounted), and these are connected with long cables. On the link ports I had incorrectly used the long "inverter > battery" cables, rather than the "battery > battery" cables. (I am surprised it ever worked at all before!)
Sorry for wasting time, and a good lesson to always read what it says on the cable before just plugging in...
6 out of 6 all working
lifeingalicia avatar image
lifeingalicia answered ·
Definately the C have to be in front.
The 2000B is now called 2000 but there was a firmware upgrade to B+.
You may want to try contact Pylon on this one.
I also remember some comments that the can bus cables where different typ A and type B.
https://community.victronenergy.com/questions/25637/problem-with-mixing-pylontech-us2000b-plus-2018-an.html
If you can ty 2 C´s and one B and see if GX see the B you know its coms.